Electricity grid operators, such as the
Electric Reliability Council of Texas (ERCOT), which operates the
Texas Interconnection grid, use a mix of generation sources, sometimes referred to as a generation,
dispatch, or supply "stack", to balance generation supply to load demand. The generation stack used on a grid varies from moment to moment based on the demand load, available generation resources, and
generation supply cost.
The generation stack can be represented and charted in different ways. It can be charted by the
type of energy source, for example: nuclear; coal; gas; wind; hydro; and solar. A generation stack might also be charted by the
differing types of power generation used at any given moment, for instance: the
continuous base load generation used to meet daily
minimum demand; the
intermediate load following generation used to supply additional power demands above the minimum requirement during a day; and
peaking generation (peakers) which only generate power during peak demand periods. The
combination of oil, gas, and coal (nuclear may also be included) generation is sometimes referred to as a "
thermal stack" as they convert fuel into heat which is then converted into mechanical energy for generating electricity.
Within the daily generation supply stack are intermittent renewable resources of power generation. Due to their intermittent output, clean renewable solar and wind generation primarily serve to
reduce the use of polluting nonrenewable fossil fuels. When wind speed is high or solar output strong, wind and solar can dramatically reduce the use of other energy sources. When wind or solar is low, grid operators need to have sufficient conventional generation or grid energy storage available to
meet demand reliably under those conditions. No source of power generation can be online generating power all of the time. None produce their maximum rated capacity continuously each having a
capacity factor. This is why grid operators need to have sufficiently reliable
reserve capacity to avoid blackouts. Texas has allowed
reserve capacity to decline over a number of years.
Widespread outages, due to the winter storm in Texas, began at 1:25 a.m. on February 15, 2021 and gradually improved as temperatures started to rise on February 18th. The fact that wind and solar electricity generation is intermittent and varies from season to season, month to month, day to day, and throughout the day is well known and for obvious reasons. Other sources of electricity generation can be intermittent as well due to fuel supply shortages, equipment failures, and routine maintenance taking generation offline. All of the above happened in Texas and a good deal more.
Now, some wild claims have been made regarding renewable energy performance during the Texas winter storm. "
Wind and solar production dropped by about 98% during the cold snap", later revised to "
90+%". "
Solar production was pretty much non-existent."
Let's see what happened from Sunday February 14th, the day before the massive rolling power outages, when ERCOT was generating enough power to hold the grid together; then on Monday Feb. 15th when rolling outages began; thru February 18th of that week. **
Daily Power Generation by Source in Megawatt-hours (MWh) Sunday, Feb. 14th - Natural Gas = 899,328 / Coal = 262,149 / Nuclear = 123,347 / Wind (174,601) + Solar (6,333) = 180,934
Monday, Feb. 15th - Natural Gas = 759,708 / Coal = 204,655 / Nuclear = 98,394 / Wind (73,395) + Solar (20,134) = 93,529
Tuesday, Feb. 16th - Natural Gas = 692,091 / Coal = 175,435 / Nuclear = 90,819 / Wind (90,087) + Solar (13,403) = 103,490
Wednesday, Feb. 17th - Natural Gas = 719,414 / Coal = 176,003 / Nuclear = 91,184 / Wind (61,184) + Solar (23,100) = 84,284
Thursday, Feb. 18th - Natural Gas = 757,320 / Coal = 196,583 / Nuclear = 110,991 / Wind (141,446) + Solar (17,831) = 159,277
* To get the
hourly average MWh to compare with ERCOT's
Seasonal Assessment of Resource Adequacy winter planning forecasts (linked in a post below), just divide any numbers above by 24.
** Revised on June 12th. Some data was very slightly off due to neglecting to select correct time zone (CST vs EST). Now corrected.
The attached graphs contain ERCOT data supplied by ERCOT or the U.S. Energy Information Administration